Title: Air/Vent Stack
Post by: anonymous on June 13, 2014, 06:20:13 PM
Had a new toilet installed and they replaced the vent/air stack. Problem is they used 100mm instead of 50mm like every other house on the street. They explain it helps toilet flush better? Comments please?
Title: Re: Air/Vent Stack
Post by: integrated on June 13, 2014, 11:22:54 PM
it does - but who cares i would be more worried about the weather proofing on that penetration through the wall
Title: Re: Air/Vent Stack
Post by: anonymous on June 14, 2014, 09:20:53 AM
You bring up a valid point,only wish the plumbing investigator we had to bring in had put that in his report. Is the plumber responsible for repairing the flashing surrounding the pipe?
Title: Re: Air/Vent Stack
Post by: gordyplum on June 14, 2014, 09:55:19 AM
A"plumbing inspector" just for that. What other problems are there to justify that?
Title: Re: Air/Vent Stack
Post by: anonymous on June 14, 2014, 10:06:29 AM
Please check out my other posts for other issues and pictures. Feedback is always appreciated
Title: Re: Air/Vent Stack
Post by: Enn on June 14, 2014, 01:00:47 PM
80mm is the minimum requirement  for a terminal vent Under G-13.

Penetration should have been flashed/sealed. External moisture.

Looking at your posts id  say the inspector will be busy, Is any of this work consented?

A look at the property file would be interesting.








Title: Re: Air/Vent Stack
Post by: anonymous on June 14, 2014, 01:10:00 PM
Inspector as been looked at work listened to our issues but seemed more intetested in mediating a settlement between contractor behind our back because we refuse to pay remaining half of their $10k quote. His report found no issues with any of the work and with 25 years behind him the mediator in the disputes tribunal found in the  contractors favour.
Title: Re: Air/Vent Stack
Post by: anonymous on June 14, 2014, 01:21:07 PM
Sorry by consent I assume you mean council? Work was all on private land so council was never involved