Had a new toilet installed and they replaced the vent/air stack. Problem is they used 100mm instead of 50mm like every other house on the street. They explain it helps toilet flush better? Comments please?
-
it does - but who cares i would be more worried about the weather proofing on that penetration through the wall
-
You bring up a valid point,only wish the plumbing investigator we had to bring in had put that in his report. Is the plumber responsible for repairing the flashing surrounding the pipe?
-
A"plumbing inspector" just for that. What other problems are there to justify that?
-
Please check out my other posts for other issues and pictures. Feedback is always appreciated
-
80mm is the minimum requirement for a terminal vent Under G-13.
Penetration should have been flashed/sealed. External moisture.
Looking at your posts id say the inspector will be busy, Is any of this work consented?
A look at the property file would be interesting.
-
Inspector as been looked at work listened to our issues but seemed more intetested in mediating a settlement between contractor behind our back because we refuse to pay remaining half of their $10k quote. His report found no issues with any of the work and with 25 years behind him the mediator in the disputes tribunal found in the contractors favour.
-
Sorry by consent I assume you mean council? Work was all on private land so council was never involved